This engineering brief demonstrates how to install an RJ45 connector onto shielded CAT 6 cable commonly found in industrial automation. This is a continuation of a previous article that explored how to remove the PUR jacket without nicking the conductor’s insulation. The fastidious workmanship carries over to the featured Ethernet cable.
If the wire insulation is nicked, it’s garbage.
Start over.
Limitations
The featured Weidmüller CST tool becomes increasingly difficult to use as the cable diameter increases. Refer to this article for an alternative method using a Weidmüller sheathing stripper
Featured Products
The featured Ethernet products are shown in Figure 1:
This article is part of the DigiKey Field Guide for Industrial Automation
Location: Teach It → Shop Practices
Difficulty:
Student — difficulty levels explained
Author: Aaron Dahlen | MSEE | Senior Applications Engineer, DigiKey
Last update: 02 Nov 2026
Figure 1: LAPP shielded Ethernet cable and RJ45 connector.
Compression clamp
Begin by installing the cable gland and clamping ring. As shown in Figure 1, there are two plastic compression clamps. I recommend you test fit the cable to select the appropriate ring. Recall that the compression is required to prevent twisting of the finished cable. I found that the four-prong ring was the correct choice. It was an uncomfortably tight fit but necessary as the cable spun even when the two-prong ring was fully compressed by the gland.
Tech Tip: Forgetting to install the compression components will cause delay as you rework the cable. There is risk of compromising the installation if the twisted pair assembly is damaged and then reused.
Are you willing to risk the installation after prying the twisted pair out of their resting positions?
We have all been there.
Wire Stripping
As described in the prerequisite article, the blades of the wire stripping tool are set via the setscrews. I found this to be the hardest and most time-consuming part of the assembly process. As seen in Figure 2, it took several attempts to properly align the blades. Some of the sacrificial wire is shown in the picture.
Figure 2: Aligning the wire stripping tool to score but not cut through the associated jacket and shield.
Pass or Fail Condition
Figure 3 presents a properly stripped cable. Be sure to adhere to the principles presented in the prerequisite article.
Nicks in the conductor’s insulation are unquestionable failures.
Observe:
-
Like in the previous article, the outer PUR jacket has been scored but not cut through. This prevents nicking the cable shield.
-
The underlying twisted pair wires do not present a perfectly cylindrical surface to the cutting tool’s blade. Consequently, it is better to make a shallow cut and then clean up the remaining shield wires as opposed to cutting deeper which then risks nicking the conductor’s insulation.
-
The majority of the shield wires have been cut away. There is a compromise between a fully cut shield and a partially cut shield. The compromise reduces the risk of nicking the underlying conductor insulation. In my opinion, “majority” is the preferred condition. The stray shield wires are easily cleaned up using a pair of side cutters.
-
According to the LAPP assembly instructions, no more than 10 mm of shield may be exposed. I found 6 mm to be appropriate and achievable with the brown cartridge of the Weidmüller CST tool as shown in Figure 2.
Figure 3: The jacket is scored without being cut through and the cable shield is mostly cut away.
Tech Tip: Purchasing a dedicated wire stripping tool for each type of cable may be warranted as the tool setup takes time. There is also a certain amount of cable waste associated with the alignment process.
Remaining Operations
There is a natural order to prepare the cable for assembly. We will walk through the process using pictures.
Remove Remaining Insulation
Remove the white inner jacket to expose the twisted pair wires. This material is relatively thin and may simply be torn as shown in Figure 4.
This is your last chance to easily install the cable gland and compression ring.
Figure 4: Tear off the white sleeve.
Install the Twisted Pair Wires into the Cable Manager
Untwist the wires and insert them into the color-coded cable manager slots as shown in Figure 5. Note that the spacing between connection and shield is closer than one would initially assume. Look ahead to Figure 7 to see the distance relationships. Note that the green outer jacket must enter the screw portion of the RJ45 connector.
Failure will result in a cable that freely spins within the connector. It’s a liability as the twisted pair connections are not structural members and will break. Maybe not today, but years down the road when the cable is inadvertently bumped. The result is more confusion and delay as the technicians now have multiple unrelated problems to troubleshoot.
Figure 5: Insert the twisted pair wires into the appropriate slots.
Compress the Twisted Pair Wires
Compress the twisted pair wires. LAPP recommends a parallel press tool but also shows a plier-wrench being used. Figure 6 is an excerpt from the LAPP assembly instructions showing the technique.
Figure 6: LAPP instruction for locking the twisted pair wires into their final position.
Final Inspection
Remove the black holder and insert the wire assembly into the RJ45 block as shown in Figure 7. Be sure to clean up any stray shield wires so that they don’t accidentally make contact with a twisted pair signal wire.
Figure 7: Final inspection of the cable assembly before the clamp is installed.
Tighten the Cable Gland
Figure 8 shows the cable assembly with the clamping ring and the cable gland ready to be installed. Note that the ring is held into position relative to the RJ45 connector. It’s a clever assembly that prevents the cable from rotating as the gland is tightened. This is highly desirable as it prevents the twisted pair conductors from being damaged.
Figure 8: Cable ready for the cable gland to be tightened.
Take Pride in the Finished Product
Figure 9 presents the finished product.
- Test that the cable does not freely rotate within the RJ45 connector.
- Be sure to test using an STP Ethernet tester. Here STP implies a test for the 8 signal wires as well as the shield.
Figure 9: Final cable assembly.
Parting Thoughts
As implied in this brief, this is fussy work. Give yourself some time to learn the techniques.
If you do the job correctly, no one will every know. Miss a step, and the entire factory will know even if the failure happens 20 years down the road.