A DC supply can be split into ± voltage rails using a resistive center tap. This works for low-powered circuits with a good current balance between positive and negative loads.
When misused, it’s no longer just a power supply, it’s a space heater!
Last updated: 29 December, 2025
Engineering Takeaways
- This method breaks when the load is unbalanced or when energy efficient circuit are required.
- Imbalance requires the tap resistors to consume 2 to 10 x the load current. There comes a point where the circuit is impractical.
- Power resistors increase system cost.
- A transient current in one rail will shift the voltage on both rails. Depending on the system this could result in long term instability e.g., op amp distortion due to imbalanced supply rails.
- A balanced supply ± is often the best answer. If necessary, active circuitry could be used.
What are complementary (dual-rail) positive and negative power supplies?
A complementary power supply provides equal and opposite polarity voltages relative to a common node. This is useful for op amp circuits that often require a + 12 and -12 voltage rails. Many benchtop power supplies feature this dual-rail option with a tracking mode that allows a single control for both positive and negative outputs.
Not all benchtop supplies feature these split power rails. However, a virtual ground may be constructed to split a 24 VDC supply into ±12 V rails.
How can we make dual-rail (± 12 V) outputs from a single output power supply?
Suppose we have an op-amp circuit that requires +/- 12 VDC voltage rails. How do we provide the complementary outputs when all we have is a variable 24 VDC power supply as shown in Figure 1?
Before you say it can’t be done, consider how the power supply is constructed. Benchtop supplies such as the B&K Precision 1550 are designed for floating outputs. In an ideal world there is no electrical connection between the ground and the black and red DC outputs. Such a power supply acts like a battery where we are free to wire the terminals in any way we choose.
Figure 1: Picture of a single output regulated power supply with a resistive center tap to provide positive and negative voltages.
Tech Tip: Be careful! Unlike a battery, the general-purpose DC power supply will not accept a reverse charging current.
- Many supplies have reverse voltage (diode) protection.
- Some power supplies clamp the output voltage to the internal DC rail.
- In extreme situations, a reverse current will cause irreversible power supply damage.
Resistors are used to provide a virtual ground
Since our power supply is perfectly capable of providing a floating 24 VDC, the desired split +/- 12 VDC is a question of reference. We can use resistors to provide a virtual ground; again, with the understanding that the power supply outputs float. The center tap solution is shown in Figure 2 along with a slightly unbalanced load. The output is reasonably well balanced with voltage rails at 12.5 and -11.5 VDC relative to ground.
Figure 2: Schematic showing how the output of a 24 VDC supply is center tapped to provide +/- 12 VDC.
Limitations of the single to dual rail technique
There are some serious limitations to this technique. The most important constraint is the balance between the load’s positive and negative current demands. This has a significant impact on the resistor choice. For example, if the load is perfectly balanced with the positive and negative loads drawing the same current, the center tap resistors may have a high value such as 10 kΩ. On the other hand, if there is a great mismatch, the tap resistors must have a low value. In fact, it may be necessary to “burn” significant amounts of energy to retain the voltage balance.
Example 1 showing an unbalanced system with small currents
Our first example is taken from Figure 2. Here the load represented by constant current sources is slightly unbalanced with the load demanding 2 mA from the positive rail and 3 mA from the negative rail.
We could enter the values in the simulator to see the results as I have done with this MultisimLive example. Another solution is to dust off the circuit theory textbook and solve the system using a supernode method. The solution for the Figure 2 circuit is shown in Figure 3. In this example the circuit has been redrawn into the traditional textbook configuration with the floating power supply top-and-center. The common ground node is moved to the base of the schematic.
Figure 3: Hand-drawn schematic and supernode equation solving for the rail voltages in an unbalanced system.
Example 2 showing an unbalanced system with relatively large currents
Suppose the loads were changed to 100 and 200 mA respectively. Let’s assume that the tap resistors must consume at least ten times the load current. With that stipulation, let’s set the tap resistors to 50 Ω. I’ll leave it to you to solve the equation, however your results should show the rails at 14.5 and -9.5 VDC.
High power dissipation penalty for unbalanced systems
If this unbalance is unacceptable, we can shift to a 25 Ω pair. The rails are now at 13.25 and 10.75 VDC. We could continue to lower the resistance to improve the balance.
However, there is a catch:
P_{TapResistors} = \dfrac{E^2}{R} = \dfrac{24^2}{25 + 25} = 11.5 \ W
Those little ½ W resistors shown in Figure 1 must be increased to 10 W devices - allowing for a 2x safety margin. Together, they consume a significant portion of the power supply’s output. As some point, we pass into the zone of silliness when we consider the energy budget for a reasonable design.
Conclusion
While this center tap method works in a pinch, we spend more energy attempting to balance the rails than to power the load. Consequently, the technique has limited applicability relegated to low-power circuits.
With that said, this has been a good review of circuit theory. It expands our understanding of the floating power supply. It also answers the age-old question:
When will I ever need to use nodal analysis?
Best Wishes,
Related articles by this author
- How to select resistor pairs for op amp and voltage divider applications
- Discover the Unexpected Frequency Response of Wire Wound Resistors
- Meet the Jellybeans: The 2N3904 and 2N3906 General-Purpose Transistors
About the author
Aaron Dahlen, LCDR USCG (Ret.), serves as an application engineer at DigiKey. He has a unique electronics and automation foundation built over a 27-year military career as a technician and engineer which was further enhanced by 12 years of teaching (interwoven). With an MSEE degree from Minnesota State University, Mankato, Dahlen has taught in an ABET accredited EE program, served as the program coordinator for an EET program, and taught component-level repair to military electronics technicians. Dahlen has returned to his Northern Minnesota home and thoroughly enjoys researching and writing articles such as this.