This is a student’s first introduction to parallel circuits. Using components from DigiKey’s Industrial Automation Training Kit, students will construct a control circuit containing five parallel branches, determine branch currents from changes in total supply current, and then compare the results to the manufacturer’s datasheets. This lab occurs early in the structured learning pathways where it serves a secondary purpose of reinforcing the student’s ability to construct industrial control circuits, identify nodes, label wires, and troubleshoot.
Instructor Notes
These instructor notes document the educational intent behind the laboratory.
The lab is designed assuming the More Knowledgeable Other (MKO) is actively engaged and able to provide formative lessons to the individual as well as the classroom. Please refer to this document for additional information about the competency-based framework.
What new mental model is being developed?
This lab is designed for students to internalize KCL. The single ammeter placed in series with the +24 VDC supply creates a puzzle requiring students to differentiate between branches that are constantly energized and those that are activated via switch or pushbutton. Consequently, individual branch current measurements are inferred rather than measured directly. Stated another way, KCL is applied at nearly every point in the lab.
To date, this is the most complex circuit the students have encountered. Students gain confidence through the hand-eye-mind exercise that crosses physical circuit construction with the abstraction of the wire diagram.
The lab provides a gentle introduction to the difference between stated datasheet values and those encountered in the real world.
What observable behaviors demonstrate competence?
- The student can interpret the wire diagram to construct the control circuit without assistance.
- When prompted, the student can locate an individual wire on both the physical trainer as well as the wire diagram and vice versa.
- Wire color is correct. Blue is used for all connections except for the white-with-blue stripe wires that are permanently attached to the 24 VDC return.
- Wire labels are present that clearly show the node relationship between wire diagram and the physical assembly.
- The student can properly position the ammeter to measure total current or branch current.
- The student demonstrates a working knowledge of KCL by demonstrating the additive nature of current. Specifically, they can differentiate between a load that is always present and a load that is added via a switch or pushbutton.
- The students can locate the datasheet for each part, locate the operational circuit parameters, and then use that data to calculate the component’s power.
- The student can troubleshoot the circuit constructed in this lab. This includes identifying faults and restoring the circuit to proper operation.
- The student can locate the manufacturer’s procedure and use it to test their multimeter’s fuse(s).
Prerequisites
Before attempting this activity, students should have a working knowledge of:
- Electrical nodes with the ability to label the wires associated with a node.
- The relationship between physical wires and the wire diagram abstraction.
- Current measurement with the meter connected in series.
Chalk Talk
- Review the characteristics of a parallel circuit with an emphasis on the additive nature of the current. Be sure to anchor the lab’s ideas into Kirchhoff’s current law (KCL) explaining that the input current from the power supply is the sum of the individual branch currents.
- Review the operation of the power supply to ensure that students do not inadvertently shift to a constant current condition.
- Review multimeter operation with an emphasis on “current through” and “voltage across.”
- Demonstrate the use of the Weidmüller 1992220000 “demarcation” block and the connections to the proximity sensor.
- Review the datasheet for a representative component. Show how to read the datasheet to determine the current draw and power.
- Be sure to explain that the components used in this lab are designed for a nominal 24 VDC.
- Point out that the datasheet may specify current or power. A calculation may be required to convert from one form to the other: P (mW) = 24 × measured I (mA)
Stumbling Points
The circuit can be overwhelming. Encourage students to build the circuit in descending rung order from top to bottom. Test each rung before moving to the next. This will reinforce the idea that parallel circuits are, well, parallel and largely independent from each other. Here we assume the supply voltage does not change as additional circuits are added.
- Set the standard for use of the 3D printed wire labels. Since this is the students’ second encounter with the wire labels, a standard of “all wires must be labeled for lab credit” is recommended.
Learning Objectives
- Build the circuit from the wire diagram using the correct wire colors and node labels.
- Use KCL to account for the current drawn by each load, including the proximity sensor when its output is off.
- Measure total current and individual branch current with an ammeter.
- Compare measured current and calculated power with the manufacturer’s datasheet values.
- Find and correct wiring errors.
Learning Pathway: Industrial Automation Technician → Fundamentals
Difficulty:
Student — difficulty levels explained
Last update: 23 Oct 2026
Figure 1: Image of the PLC industrial training kit configured for the control power measurement lab.
Construction
Construct the circuit shown in Figure 2.
- Label each node using the technique described in this article.
- Use blue wires for all nodes except the Return node. The white-with-blue stripe is reserved for the Return node.
Figure 2: Wire diagram for the control power measurement lab.
Measurements
Test the fuses in your current meter following the procedure shown in the meter’s operator’s manual.
Connect the ammeter in series with the +24 supply line using the technique described in this article.
Power the circuit from a 24 VDC bench power supply set to deliver 24 VDC with a current limit of 400 mA. Note that this current limit is selected to reduce the chance of opening the meter’s fuse such as when the fan’s rotor is accidentally locked. Adjust as necessary for your given meter is using other than the pictured Fluke 87 V.
Calculate and record the current draw for each component. Start by measuring the baseline current consumed by the untriggered proximity sensor. This is the only load that cannot be turned off given the wire diagram shown in Figure 2. Subtract this baseline value from each load. For example, the current measured when pushbutton 1 is pressed is the summation of the untriggered proximity sensor and relay 1.
Calculation: P (mW) = 24 × measured I (mA)
| Load / Operating Condition | Measured Current (mA) | Calculated Power at 24 VDC (mW) | Datasheet Power (mW) |
| Proximity Sensor: | |||
| Sensor when idle | |||
| Sensor + associated relay | |||
| Fan: | |||
| Unobstructed airflow | |||
| On table — label side up | |||
| On table — label side down | |||
| Both sides blocked | |||
| Relays: | |||
| Relay 1 — energized | |||
| Relay 2 — energized | |||
| Relay 3 — energized |
Record the datasheet values into the table. State whether each value is typical, nominal, or maximum. Note that it may be necessary to calculate the power from the datasheet values for current and voltage.
Show that this lab supports KCL. This is done by comparing the summation of the individual measured current against the total measured current when all five loads are activated.
Note that this is not as clean as the typical classroom lab. You will need to state your assumptions such as fan operating unobstructed.
Work with your lab instructor to answer a few questions:
What is the purpose of this lab?
Define datasheet terms including nominal, typical, minimum, and maximum. Which datasheet values were entered into the table?
Why doesn’t the current go to zero when all switches and pushbuttons are turned off?
Under what conditions does the fan draw the least amount of current? Speculate as to why? If available, ask your lab instructor to demonstrate a related experiment using a vacuum cleaner.
Why were the fan and proximity sensor included in this lab?
Compare the total measured current against the value predicted by the datasheet. Be sure to show your work.
Move the ammeter so that it measures the current consumed by Relay 2 and no others. Present your work to the lab instructor. Contrast and compare the benefits of measuring individual branch current as opposed to the KCL summation procedure used in this lab.
Troubleshooting: Request your lab instructor inject wiring errors into the trainer. Work to troubleshoot the trainer without assistance.
DigiKey Navigation
Related Foundational Articles
AC vs DC Relay Specifications: Coil Ratings, Contact Ratings, and Common Mistakes
Relay Jumpers Cut Wiring Time and Panel Clutter
About This Author