I have got an Analyzer that using RS485 Modbus to communicate. It that possible to use any adapter or other method to change it to Profibus DP?
Yes, this is possible, but you’ll need a protocol gateway rather than a simple RS-485 adapter.
The important detail is that Modbus RTU and PROFIBUS DP are different protocols, even though both can use RS-485 electrically.
If your analyzer is a Modbus RTU slave/server and you’re connecting it to an existing PROFIBUS DP network controlled by a PLC, you’d typically need a gateway with:
Modbus RTU master/client functionality on the analyzer side.
PROFIBUS DP slave/device functionality on the PLC side.
Be careful with the direction when choosing a gateway. A product described as “PROFIBUS Master to Modbus RTU Slave” is intended for a different arrangement.
The gateway would poll the analyzer’s Modbus registers and map the resulting values into PROFIBUS input data that your PLC can read. You’ll need the analyzer’s Modbus register map and the gateway’s GSD file for the PLC configuration.
I’d also check the analyzer’s serial settings (baud rate, parity and slave address), and how its 32-bit measurements are encoded across Modbus registers. Byte and word order mismatches can make otherwise valid communication produce incorrect readings.
Before configuring PROFIBUS, I’d verify that the analyzer responds to ordinary Modbus RTU requests using a suitable RS-485 interface and Modbus test tool.
What is the analyzer’s manufacturer/model, and which PLC or PROFIBUS DP master are you connecting it to? That would make it easier to identify the correct gateway and confirm compatibility.