Tech tip: How to size a 230 V online UPS (1 to 3 kVA): power rating, batteries and backup time

A single-phase online UPS protects IPCs, HMIs, network equipment and small machine controls against power outages and mains disturbances. With double conversion the load is always supplied by the inverter, so there is no transfer gap when the mains fails. This tip shows how to size the Wöhrle AC-UPS-PS-230 series (1 to 3 kVA). It comes in two versions: -B with internal batteries, ready for connection, and a version without batteries that you equip yourself.

1. Determine the load

  • Add up the real power of all loads that must be buffered. With an output power factor of 1.0 the kVA rating equals the kW rating (1, 2 or 3 kW).
  • Plan a reserve of about 20 % for extensions and switch-on currents.
  • Do not size for overload. The datasheet allows short overloads in normal mode (102 % to 110 % for 10 min, up to 150 % for 30 s), but in battery mode only 1 min below 110 % and 5 s above.

2. Check the mains

Full output is available from 176 to 276 V AC. Between 110 and 176 V AC the output is reduced from 100 % down to 50 %.

3. Estimate the backup time

Typical values from the datasheet with new and fully charged 12 V AGM batteries at 25 °C:

UPS Batteries 50 % load (min) 100 % load (min)
1 kVA 2 × 9 Ah 10 2.5
1 kVA 3 × 7 Ah 10 3
1 kVA 3 × 9 Ah (as in -B) 17 6
2 kVA 4 × 9 Ah 10 2.5
2 kVA 6 × 7 Ah 10 3
2 kVA 6 × 9 Ah (as in -B) 17 6
3 kVA 6 × 9 Ah (as in -B) 10 2.5

At 10 % load the 1 kVA unit with 3 × 9 Ah reaches approx. 120 min. Battery age and temperature reduce the real backup time, so keep a reserve.

4. Choose the version

  • -B: ready for connection with 12 V / 9 Ah AGM batteries. The batteries are user-replaceable.
  • Without batteries: lighter to transport and install (1 kVA: 5.5 kg instead of 13.6 kg). Choose 7 Ah or 9 Ah batteries and their number to match the backup time.
  • Longer backup times: the datasheet lists the battery extensions AC-BAT-PS-06 and AC-BAT-PS-12.

5. Plan the integration

EPO and RS232 are standard. Optional SNMP, USB and RS485 adapters let you report a mains failure to the PLC or IPC for a controlled shutdown.

Example

An IPC (250 W), an HMI (50 W), a network switch (20 W) and the PLC power supply (180 W) must keep running for at least 10 minutes.

Wöhrle AC-UPS-PS-230 on DigiKey

Wöhrle part DigiKey part number Key data (datasheet)
AC-UPS-PS-230-1KVA 6141-AC-UPS-PS-230-1KVA-ND 1 kVA, for 2 or 3 batteries 12 V / 7 or 9 Ah
AC-UPS-PS-230-1KVA-B 6141-AC-UPS-PS-230-1KVA-B-ND 1 kVA, 3 × 12 V / 9 Ah, 6 min at full load
AC-UPS-PS-230-2KVA 6141-AC-UPS-PS-230-2KVA-ND 2 kVA, for 4 or 6 batteries 12 V / 7 or 9 Ah
AC-UPS-PS-230-2KVA-B 6141-AC-UPS-PS-230-2KVA-B-ND 2 kVA, 6 × 12 V / 9 Ah, 6 min at full load
AC-UPS-PS-230-3KVA 6141-AC-UPS-PS-230-3KVA-ND 3 kVA, for 6 batteries 12 V / 7 or 9 Ah
AC-UPS-PS-230-3KVA-B 6141-AC-UPS-PS-230-3KVA-B-ND 3 kVA, 6 × 12 V / 9 Ah, 2.5 min at full load

Version without batteries: AC-UPS-PS-230-2KVA Wöhrle | Uninterruptible Power Supply (UPS) Systems | DigiKey Marketplace
Which loads do you need to keep running and for how long? Post your load list and backup time here and we will help with the sizing.