Adding up the load currents is the starting point for sizing a 24 V DIN rail power supply. Whether the unit really delivers enough power in the cabinet also depends on the ambient temperature, the mounting position, peak loads and the mains conditions. This tip walks through these checks using the three-phase Wöhrle POWER-TEC 2420 (24 V / 20 A, 480 W) as an example.
1. Add up the continuous load
- Sum the currents of all 24 V loads that run at the same time.
- Include charging currents, for example of a DC UPS.
- Keep a reserve of about 20 % for extensions.
2. Check the ambient temperature
- The POWER-TEC 2420 delivers its rated 480 W from -40 °C to +60 °C with convection cooling only.
- Between +60 °C and +70 °C the output must be derated according to the curve in the datasheet.
- Up to 45 °C a thermal power bonus of 120 % is available (576 W / 24 A). Treat it as a reserve. Do not use it as the basis of your design if the cabinet can get warmer than 45 °C.
3. Check peak loads
Motors and large capacitive loads draw high currents for a short time. The Power Boost of the POWER-TEC 2420 supplies up to 150 % for 5 s (at 400 to 480 V AC or 500 V DC and -40 °C to +60 °C). For the 20 A unit this means up to 30 A for 5 s. The continuous load must still stay within the rated current.
4. Mount it correctly
- Standard mounting position: input terminals at the bottom.
- Keep a clearance of 20 mm above and 40 mm below the unit for convection. No lateral spacing between units is required.
- Other mounting positions can require a reduced output current. Check the datasheet before you deviate from the standard position.
5. Consider the mains
The input voltage range is 3 × 320 to 575 V AC. If one phase fails, the POWER-TEC 2420 keeps running on two phases with up to 340 W output. If the machine must keep running during a phase failure, size the continuous load for this value.
Example
A machine has these continuous 24 V loads:
| Load | Continuous current |
| PLC and I/O modules | 4 A |
| HMI panel | 1.5 A |
| Valve terminal | 5 A |
| Sensors | 2 A |
| Small servo drive | 3 A |
| Total | 15.5 A (372 W) |
- 15.5 A on a 20 A unit is 78 % load. That leaves a reserve of about 22 %.
- The cabinet reaches up to 55 °C in summer. The full 480 W are available, but the thermal bonus is not.
- When the drive starts, the total current rises to 25 A for 2 s. This is within the Power Boost (30 A for 5 s).
- Phase failure: 372 W is above the 340 W of two-phase operation. If the machine must keep running in this case, choose the POWER-TEC 2440. Its datasheet allows up to 600 W in two-phase operation.
Result: the POWER-TEC 2420 fits if a phase failure may stop the machine. Otherwise the POWER-TEC 2440 covers the two-phase case.
Wöhrle POWER-TEC DIN rail power supplies on DigiKey
| Wöhrle part | DigiKey part number | Key data |
| POWER-TEC 2410 | 6141-POWER-TEC2410-ND | 24 V / 10 A / 240 W |
| POWER-TEC 2420 | 6141-POWER-TEC2420-ND | 24 V / 20 A / 480 W, 576 W up to 45 °C, boost 150 % for 5 s, two-phase operation up to 340 W |
| POWER-TEC 2440 | 6141-POWER-TEC2440-ND | 24 V / 40 A / 960 W, boost 150 % for 5 s, two-phase operation up to 600 W |
| POWER-TEC 4810 | 6141-POWER-TEC4810-ND | 48 V / 10 A / 480 W |
| POWER-TEC 4820 | 6141-POWER-TEC4820-ND | 48 V / 20 A / 960 W |
What reserve do you plan for 24 V power supplies in your cabinets? Questions about a specific application are welcome here.