Tech tip: Line-interactive or online UPS? Choosing a 230 V AC UPS for IPCs and controls

A single-phase AC UPS protects IPCs, HMIs, network devices and small controls against power failures. The first decision is the topology: line-interactive or online double conversion. Both bridge an outage with a battery. They differ in what the load sees in normal operation and at the moment the mains fails. This tip compares the two using the Wöhrle UPS SimpLi series (line-interactive, 600 to 1500 VA) and the AC-UPS-PS-230 series (online, 1 to 3 kVA).

1. Understand the difference

  • Line-interactive: in normal operation the load is supplied from the mains. An automatic voltage regulator (AVR) corrects over- and undervoltage. When the mains fails, the inverter takes over after a short transfer time. The UPS SimpLi switches over in typ. 6 ms and delivers a pure sine wave.
  • Online double conversion: the inverter supplies the load all the time. The AC-UPS-PS-230 has a transfer time of 0 ms from mains to battery. Its output THDu is ≤ 2 % with linear loads.

In the terms of IEC 62040-3, line-interactive designs usually fall into class VI and double conversion designs into class VFI.

2. Check your loads

  • Switched-mode power supplies usually ride through a few milliseconds with their own hold-up time. Check the value in the datasheet of each device.
  • If no interruption at all is acceptable, choose online.
  • Add up the real power in watts. The UPS SimpLi is rated with a power factor of 0.7 (for example 800 VA / 560 W). The AC-UPS-PS-230 has an output power factor of 1.0, so 1 kVA means 1 kW.

3. Check your mains and the location

  • UPS SimpLi: input range 160 to 290 V AC at 45 to 65 Hz. In mains mode the output frequency follows the mains.
  • AC-UPS-PS-230: full output from 176 to 276 V AC, operation down to 110 V AC with reduced output. The inverter regulates the output frequency.
  • Weak grids, frequent voltage fluctuations or a generator supply point to online.
  • The UPS SimpLi is specified for 0 to 40 °C ambient.

4. Plan the shutdown

  • UPS SimpLi: USB port, shutdown software for Windows, Linux and Mac OS.
  • AC-UPS-PS-230: EPO and RS232 as standard. SNMP, USB, RS485 and a dry contact interface are optional.

Quick decision guide

Criterion Line-interactive (UPS SimpLi) Online (AC-UPS-PS-230)
Transfer time mains to battery typ. 6 ms 0 ms
Output frequency in mains mode follows the mains regulated by the inverter
Output power factor 0.7 1.0
Choose it for PCs, workstations, network equipment on stable mains IPCs and controls on weak mains or generator supply

Example

A test bench with a measurement PC, a monitor and instruments draws 350 W. After a power failure the data must be saved and the PC shut down.

  • USV-SIMPLI-800 VA (800 VA / 560 W): 350 W is about 63 % load. The backup time lies between 4 min (50 % load) and 2 min (75 % load). That is enough for an automated shutdown via USB.
  • Same 350 W at a machine with a generator supply, where the controls must keep running without any interruption: AC-UPS-PS-230-1KVA-B. 350 W is 35 % load. The datasheet gives 30 min at 300 W and 21 min at 400 W.

Wöhrle AC UPS on DigiKey

Wöhrle part DigiKey part number Key data (datasheet)
USV-SIMPLI-600VA 6141-USV-SIMPLI-600VA-ND Line-interactive, 600 VA / 420 W, 7 min at 50 % load
USV-SIMPLI-800 VA 6141-USV-SIMPLI-800VA-ND Line-interactive, 800 VA / 560 W, 4 min at 50 % load
USV-SIMPLI-1500VA 6141-USV-SIMPLI-1500VA-ND Line-interactive, 1500 VA / 1050 W, 4 min at 50 % load
AC-UPS-PS-230-1KVA-B 6141-AC-UPS-PS-230-1KVA-B-ND Online, 1 kVA / 1 kW, 3 × 12 V / 9 Ah, 17 min at 50 % load
AC-UPS-PS-230-2KVA-B 6141-AC-UPS-PS-230-2KVA-B-ND Online, 2 kVA / 2 kW, 6 × 12 V / 9 Ah, 17 min at 50 % load
AC-UPS-PS-230-3KVA-B 6141-AC-UPS-PS-230-3KVA-B-ND Online, 3 kVA / 3 kW, 6 × 12 V / 9 Ah

Which loads do you protect with an AC UPS, and can they tolerate a transfer time of a few milliseconds? Post your application here and we will help with the selection.