A single-phase AC UPS protects IPCs, HMIs, network devices and small controls against power failures. The first decision is the topology: line-interactive or online double conversion. Both bridge an outage with a battery. They differ in what the load sees in normal operation and at the moment the mains fails. This tip compares the two using the Wöhrle UPS SimpLi series (line-interactive, 600 to 1500 VA) and the AC-UPS-PS-230 series (online, 1 to 3 kVA).
1. Understand the difference
- Line-interactive: in normal operation the load is supplied from the mains. An automatic voltage regulator (AVR) corrects over- and undervoltage. When the mains fails, the inverter takes over after a short transfer time. The UPS SimpLi switches over in typ. 6 ms and delivers a pure sine wave.
- Online double conversion: the inverter supplies the load all the time. The AC-UPS-PS-230 has a transfer time of 0 ms from mains to battery. Its output THDu is ≤ 2 % with linear loads.
In the terms of IEC 62040-3, line-interactive designs usually fall into class VI and double conversion designs into class VFI.
2. Check your loads
- Switched-mode power supplies usually ride through a few milliseconds with their own hold-up time. Check the value in the datasheet of each device.
- If no interruption at all is acceptable, choose online.
- Add up the real power in watts. The UPS SimpLi is rated with a power factor of 0.7 (for example 800 VA / 560 W). The AC-UPS-PS-230 has an output power factor of 1.0, so 1 kVA means 1 kW.
3. Check your mains and the location
- UPS SimpLi: input range 160 to 290 V AC at 45 to 65 Hz. In mains mode the output frequency follows the mains.
- AC-UPS-PS-230: full output from 176 to 276 V AC, operation down to 110 V AC with reduced output. The inverter regulates the output frequency.
- Weak grids, frequent voltage fluctuations or a generator supply point to online.
- The UPS SimpLi is specified for 0 to 40 °C ambient.
4. Plan the shutdown
- UPS SimpLi: USB port, shutdown software for Windows, Linux and Mac OS.
- AC-UPS-PS-230: EPO and RS232 as standard. SNMP, USB, RS485 and a dry contact interface are optional.
Quick decision guide
| Criterion | Line-interactive (UPS SimpLi) | Online (AC-UPS-PS-230) |
|---|---|---|
| Transfer time mains to battery | typ. 6 ms | 0 ms |
| Output frequency in mains mode | follows the mains | regulated by the inverter |
| Output power factor | 0.7 | 1.0 |
| Choose it for | PCs, workstations, network equipment on stable mains | IPCs and controls on weak mains or generator supply |
Example
A test bench with a measurement PC, a monitor and instruments draws 350 W. After a power failure the data must be saved and the PC shut down.
- USV-SIMPLI-800 VA (800 VA / 560 W): 350 W is about 63 % load. The backup time lies between 4 min (50 % load) and 2 min (75 % load). That is enough for an automated shutdown via USB.
- Same 350 W at a machine with a generator supply, where the controls must keep running without any interruption: AC-UPS-PS-230-1KVA-B. 350 W is 35 % load. The datasheet gives 30 min at 300 W and 21 min at 400 W.
Wöhrle AC UPS on DigiKey
| Wöhrle part | DigiKey part number | Key data (datasheet) |
|---|---|---|
| USV-SIMPLI-600VA | 6141-USV-SIMPLI-600VA-ND | Line-interactive, 600 VA / 420 W, 7 min at 50 % load |
| USV-SIMPLI-800 VA | 6141-USV-SIMPLI-800VA-ND | Line-interactive, 800 VA / 560 W, 4 min at 50 % load |
| USV-SIMPLI-1500VA | 6141-USV-SIMPLI-1500VA-ND | Line-interactive, 1500 VA / 1050 W, 4 min at 50 % load |
| AC-UPS-PS-230-1KVA-B | 6141-AC-UPS-PS-230-1KVA-B-ND | Online, 1 kVA / 1 kW, 3 × 12 V / 9 Ah, 17 min at 50 % load |
| AC-UPS-PS-230-2KVA-B | 6141-AC-UPS-PS-230-2KVA-B-ND | Online, 2 kVA / 2 kW, 6 × 12 V / 9 Ah, 17 min at 50 % load |
| AC-UPS-PS-230-3KVA-B | 6141-AC-UPS-PS-230-3KVA-B-ND | Online, 3 kVA / 3 kW, 6 × 12 V / 9 Ah |
Which loads do you protect with an AC UPS, and can they tolerate a transfer time of a few milliseconds? Post your application here and we will help with the selection.