Tech tip: Setting electronic circuit breakers (e-fuses) for 24 V DC load circuits

In 24 V DC control circuits, conventional miniature circuit breakers often do not trip reliably: their magnetic trip needs a multiple of the rated current (typically 3 to 5 × In for a B characteristic), while a switched-mode power supply limits its output current to little more than its rating. The result is a voltage drop that affects all loads instead of a selective disconnection of the faulty circuit. Electronic circuit breakers (e-fuses) solve this, but they must be set correctly. Here is a step-by-step approach.

1. List the load circuits

For each circuit note the continuous current, the inrush current (capacitive loads, motors, valve terminals, lamps) and the cable cross-section and length.

2. Set the trip current

  • Trip current ≈ 1.25 × continuous current of the circuit (rounded up to the next available setting)
  • The trip current must not exceed the current-carrying capacity of the cable
  • Prefer one circuit per device group, so a fault only switches off the affected part of the machine

3. Handle inrush currents

  • Use a slower trip characteristic or the boost function for loads with high inrush currents
  • Check the maximum capacitive load in the datasheet: large input capacitors of drives or IPCs can trip a fast characteristic
  • A sequential switch-on of the channels reduces the total inrush current seen by the power supply

4. Size the power supply

  • Sum of all continuous currents ≤ rated current of the power supply, with a reserve of about 20 %
  • The trip settings of all channels may add up to more than the power supply rating, as long as the simultaneous continuous load does not
  • Unlike circuit breakers, e-fuses do not need a high short-circuit current from the power supply to trip

5. Signalling and reset

Decide whether a tripped channel should be reported to the PLC (DC OK / relay contact) and whether it should be reset manually on site or remotely.

Example

24 V / 20 A power supply with four circuits, using a 4-channel e-fuse with settings 1/2/4/6/8/10 A:

Circuit Continuous current Setting
PLC and I/O modules 3 A 4 A
HMI panel 1.5 A 2 A
Valve terminal (inrush) 4 A 6 A
Sensors 1 A 2 A
Total 9.5 A n/a

The continuous load of 9.5 A leaves enough reserve on the 20 A power supply, and each channel switches off selectively in the event of a fault.

Wöhrle electronic circuit breakers on DigiKey

Wöhrle part DigiKey part number Key data
ESB10.2 6141-ESB10.2-ND 2 channels, 10 to 31 V DC, 2/4/6/10 A per channel, trip characteristic selectable via USB
ESB10.4 6141-ESB10.4-ND 4 channels, 18 to 30 V DC, 1/2/4/6/8/10 A per channel (rotary switch), boost up to 130 %
POWER-TEC10.4 6141-POWER-TEC10.4-ND 4 channels, 22 to 28 V DC, up to 10 A per channel (continuously adjustable), boost 150 % for 5 s, LED load indication, relay contact
ESB10.8 6141-ESB10.8-ND 8 channels, 24 V DC (7 to 30 V), 0.5 to 10 A per channel, max. 80 A total (70 A acc. to UL 2367)
ESB10.8-48 6141-ESB10.8-48-ND 8 channels, 48 V DC (28 to 58 V), 0.5 to 10 A per channel

Please check the datasheets on the DigiKey product pages for the exact trip characteristics and the maximum capacitive load. Questions about a specific application are welcome here. More Wöhrle products on DigiKey: Wöhrle Power Systems Distributor | DigiKey