Tech tip: Supercapacitor or battery for a 24 V DC UPS? Estimating the buffer time

A 24 V DC UPS keeps controllers, IPCs, HMIs and sensors running when the mains fails. The first design decision is the energy storage: supercapacitors or batteries. This tip shows how to choose and how to estimate the buffer time.

1. Define the requirement

  • Load power P = 24 V × load current (only the loads that must be buffered)
  • Required time: bridging voltage dips (milliseconds), a controlled shutdown of an IPC or saving data (seconds to about one minute), or continued operation during an outage (minutes to hours)
  • Ambient temperature and the maintenance effort that is acceptable

2. Supercapacitor buffer: estimate the time from the stored energy

For supercapacitor modules the buffer time follows from the usable energy E and the load power P:

t ≈ E / P

Example: a module with 5.8 kJ supplies a 240 W load (24 V / 10 A) for about 5800 J / 240 W ≈ 24 s; at 120 W the time roughly doubles. Plan a reserve of about 20 % for capacitor ageing, temperature and conversion losses. For short dips, the datasheets usually state the buffer time directly at given load currents.

Wöhrle part DigiKey part number Stored energy / buffer time (datasheet)
UGVC2420NG 6141-UGVC2420NG-ND 24 V / 20 A: 350 ms at 20 A, 700 ms at 10 A
UGVC2440 6141-UGVC2440-ND 24 V / 40 A, 180 J: 400 ms at 40 A, 1.4 s at 10 A
UGVC2440-2 6141-UGVC2440-2-ND 24 V / 40 A, 180 J: 300 ms at 40 A, 1 s at 10 A
UGVC2401 6141-UGVC2401-ND Power supply 80 to 264 V AC with buffer, 24 V / 1 A, 0.6 kJ: approx. 25 s at 1 A
UGVC2425P 6141-UGVC2425P-ND 24 V / 25 A, 1.2 kJ
UGVC2440P 6141-UGVC2440P-ND 24 V / 40 A, 4.0 kJ
UGVC2410-5,8KJ 6141-UGVC2410-5,8KJ-ND 24 V / 10 A, 5.8 kJ: approx. 24 s at 10 A
UGVC2410-13,4KJ 6141-UGVC2410-13,4KJ-ND 24 V / 10 A, 13.4 kJ: approx. 56 s at 10 A

Supercapacitors are maintenance-free, tolerate frequent charge/discharge cycles and recharge within seconds to minutes. This makes them well suited for dips and controlled shutdowns.

3. Battery backup: use the discharge table, not only the Ah rating

For batteries the backup time is not simply capacity ÷ current: at higher currents the usable capacity drops noticeably. Use the backup time tables in the datasheets, for example:

Load current BE2401NG (24 V / 1.2 Ah) BE2402NG (24 V / 2.2 Ah)
1 A approx. 36 min approx. 60 min
2.5 A approx. 15 min approx. 28 min
5 A approx. 5 min approx. 6 min
10 A n/a approx. 3 min

For longer times, larger lead-acid modules from 7.2 Ah up to 80 Ah are available (BE2407NG to BE2480NG). Also check:

  • Charging: the DC UPS controller must suit the battery capacity and chemistry. Example: the UNG2403 (24 V / 3 A) is designed for lead-acid batteries from 1.2 Ah to 6 Ah.
  • Service life: VRLA lead-acid batteries are typically replaced every 3 to 5 years; high ambient temperatures shorten their life considerably. Mount them in the coolest place of the cabinet.
  • Lithium iron phosphate (LiFePO4) such as the BE2403Li (25.6 V / 3.3 Ah, recommended -20 °C to +45 °C) offers a higher cycle life, but requires a controller with a suitable charging profile.

4. Quick decision guide

Requirement Recommended storage
Bridge voltage dips (ms to a few s) Supercapacitor buffer (e.g. UGVC2420NG, UGVC2440)
Controlled shutdown / save data (s to approx. 1 min) Supercapacitor kJ modules (UGVC2425P, UGVC2440P, UGVC2410)
Continue operation during an outage (min to h) DC UPS controller + battery module (UNG series + BE series)
Little or no maintenance, high ambient temperature Supercapacitor

Questions about a specific application? Post your load current and required buffer time here. We are happy to help with the sizing. Further Wöhrle DC UPS products on DigiKey: https://www.digikey.com/en/supplier-centers/wohrle