The relay operating voltage is *% max, the release voltage is *% or higher. What is the difference?

Question:

Why does the product catalog say that the relay operating voltage is *% max. and the release voltage is *% or higher?

Block

Answer:

The operating voltage is such that the relay will always operate when a voltage higher than that value is applied, and the release voltage is such that the relay will always release when a voltage lower than that value is applied.

Block

Explanation:

To turn ON/OFF reliably:
To guarantee that the relay operates and releases, apply *% or more of the rated voltage when turning it on, and apply *% or less of the rated voltage when turning it off.

G5NB specifications for must-operate/release voltages

Using G5NB as an example:
Operate voltage 75% max., release voltage 10% or less (value when coil temperature is +23°C)
When the rated coil voltage is 24 VDC:

  • [Operate voltage] If it is 24 x 0.75 = 18 V or more, all relays operate.
  • [Release voltage] If it is 24 x 0.1 = 2.4 V or less, all relays release.

The operate/release voltage characteristics indicate the characteristics of the relay and should be used within the allowable voltage range.
Also, the voltage should be basically zero when it is OFF. Do not leave any residual voltage.

Test method
The test methods for the operating voltage and release voltage conform to the JIS standard (C5442-1996).

Block

Quick tips

The relay may operate even if the rated voltages are not applied, but operation may become unstable and the risk of failure increases.

Block