CUI Devices omniCOOL™ C, CF, V Series Fan Comparison & Life Expectancy
Sleeve and ball bearings are the most common types of fan bearings. Ball bearings are the standard by which other small-fan bearing systems are judged. Various tweaks and augmentations to the basic sleeve bearing concept have been made in an effort to obtain ball bearing-like longevity at sleeve bearing cost and noise levels, with varying degrees of success.
Unless a fan (or other bearing type) strictly lists “ball” bearing or “roller” bearing then you can assume it is based on a bushing or sleeve design. As an example, a spherical bearing is actually more of a spherical bushing since it has no internal moving parts, unless it is listed as spherical “roller” bearing.
Since ball bearing fans are less cost savvy and “standard” sleeved fans have shorter life expectancy, the CUI omniCOOL™ fan series are offered as a cost-performance tradeoff between traditional sleeve and ball bearing designs. The Enhanced Sleeve Bearing of “C” or “CF” series is offered as a replacement for standard sleeve bearing fans while the Magnetic Structure (magnetic rotor-balancing) design of the “V” series, although based around a sleeved design, is offered as a potential replacement for both standard sleeve and ball bearing fans.
Example Series Suffixes:
CFM-80C
CFM-80CF
CFM-80V
“C” and “CF” suffixed series are a (modified) sleeve bearing design. These feature an “Enhanced Bearing” sleeve, which incorporate specialized grooves on the outside of the bearing that assist with circulation of lubricant around the shaft. This improved circulation also works to reduce friction and build-up of lubricant, leading to more efficient operation and longer life expectancy compared to traditional sleeve bearing designs. Common with all standard sleeve bearing types, have a much shorter lifespan in general as compared to ball bearing fans, especially if the fan is not operated vertically (horizontal impeller shaft) or is used in contaminating environments lacking an IP rating. However sleeved fans are more economical and offer more protection from impacts, they also produce less noise initially until they begin to wear out.
“V” suffixed series are a sleeve bearing design but that also utilizes a “Magnetic Structure” (magnetic rotor-balancing) design and offer longer life expectancy than the C or CF series and other regular sleeve bearing designs since the magnetic structure effectively makes the rotor work like a spinning top – but one that never falls over and one that can operate at any angle. The magnetic structure sits in front of the rotor and, because its flux is parallel to the direction of the rotor shaft, it uniformly attracts the entire rotor, at whatever angle the fan unit is being held. The shaft and bearing sleeve no longer bear the weight of the rotor, which is instead suspended in the air which dramatically reduces the friction between the shaft and the inside of the bearing. Additionally, the magnetic field works to lower the center of gravity by pulling the shaft downward, minimizing the tilt and wobble issues that exist with traditional sleeved bearings.
See also:
Source - omniCOOL™ Bearing System
CUI - Fan Bearing Types – Weighing the Pros and Cons
Calculating Airflow/CFM
Orion Fan Wire Color Codes and Special Functions
Fan Bearings & Longevity
How to Select a Fan for Forced Air Cooling
Orion Fans Part Number Configurator
Orion Fans Technical Terms
Fans: Air Flow vs Static Pressure
All DC Brushless Fans (BLDC)
Suggested Resources for Fan Selection and Application
Fan Features
Fans - Finger Guards, Filters & Sleeves
Fans - Accessories
Part Numbers
102-4383-ND
2223-CFM-4010C-050-195-20-ND
2223-CFM-4010C-165-251-20-ND
CFM-5015V-132-154-ND
CFM-5015V-161-330-ND
CFM-5010V-043-260-ND
CFM-6025V-125-107-ND
CFM-4010V-058-206-ND
CFM-4010V-170-273-ND
CFM-8025V-126-280-ND
CFM-8025V-129-300-ND
2223-CFM-6010C-130-215-ND
2223-CFM-4010C-065-251-ND
2223-CFM-3510CF-170-222-22-ND
2223-CFM-6010C-150-326-ND
2223-CFM-6010C-140-278-20-ND
CFM-4020V-145-123-11-ND
2223-CFM-2507CF-0140-313-20-ND
2223-CFM-7015C-230-295-ND
2223-CBM-5020C-150-320-ND
CFM-9225V-124-280-ND
2223-CFM-4010C-180-296-ND
2223-CFM-2507CF-0100-240-ND
2223-CFM-2507CF-050-089-ND
CFM-4010V-058-206-11-ND
CFM-4010V-070-273-11-ND
CFM-4010V-158-206-11-ND
CFM-4010V-170-273-11-ND
2223-CFM-6010C-150-326-20-ND
2223-CFM-4010C-150-195-20-ND
CFM-4010V-150-157-11-ND
2223-CFM-8025C-130-330-ND
2223-CFM-4020CF-035-114-ND
2223-CFM-4020CF-255-212-ND
2223-CFM-3510CF-160-188-22-ND
2223-CFM-8015CF-230-301-ND
2223-CFM-7015C-250-406-20-ND
2223-CFM-6015CF-235-278-ND
2223-CFM-6015CF-225-204-ND
CFM-4010V-185-314-11-ND
102-5604-ND
2223-CFM-4010C-080-296-20-ND
2223-CFM-7015C-240-357-20-ND
2223-CFM-5015CF-130-224-20-ND
2223-CFM-4020CF-235-114-20-ND
2223-CFM-5015CF-145-312-20-ND
2223-CFM-4020CF-055-212-20-ND
2223-CFM-2507CF-1100-240-ND
2223-CFM-2507CF-170-163-ND
2223-CFM-6015CF-255-375-ND
CFM-8025V-226-280-ND
2223-CBM-4010C-140-178-ND
2223-CFM-5015CF-160-374-ND
2223-CFM-4020CF-075-306-ND
2223-CFM-4020CF-295-342-ND
2223-CFM-4020CF-275-306-20-ND
2223-CFM-7015C-130-295-20-ND
CFM-4010V-185-314-20-ND
2223-CBM-5015CF-035-293-ND
2223-CBM-5015CF-045-348-ND
2223-CBM-5015CF-135-293-ND
2223-CBM-5015CF-145-348-ND
CFM-6010V-130-205-ND
2223-CFM-4020CF-095-342-20-ND
2223-CBM-4010C-160-267-20-ND
2223-CBM-4010C-140-178-20-ND
2223-CBM-5015CF-045-348-22-ND
2223-CFM-8015CF-220-213-ND
2223-CFM-8015CF-120-213-ND
2223-CBM-5015CF-155-391-ND
2223-CBM-5015CF-055-391-ND
2223-CBM-4010C-150-227-ND
2223-CFM-2507CF-1140-313-20-ND
2223-CFM-9225C-125-317-ND
2223-CBM-7530CF-240-454-20-ND
2223-CBM-5015CF-035-293-20-ND
2223-CBM-5015CF-045-348-20-ND
2223-CBM-5015CF-145-348-20-ND
2223-CFM-8015CF-240-363-ND
2223-CFM-6025CF-035-274-ND
2223-CFM-8015CF-140-363-ND
2223-CFM-6025CF-150-351-ND
2223-CFM-7015C-030-295-ND
2223-CFM-7015C-140-357-ND
2223-CBM-3507CF-145-139-ND
2223-CBM-5020C-140-305-ND
2223-CBM-3507CF-045-139-ND
2223-CBM-3507CF-155-183-ND
2223-CBM-3507CF-055-183-ND
CFM-6015V-139-292-ND
2223-CFM-3007CF-0110-320-ND
CFM-4020V-060-210-ND
CFM-4020V-070-255-ND
CFM-4020V-150-165-ND
CFM-4020V-160-210-ND
2223-CBM-4010C-150-227-20-ND
2223-CBM-5015CF-155-391-20-ND
2223-CBM-5015CF-055-391-20-ND
2266-CFM-8020V-146-480-ND,102-4381-ND
2223-CBM-4010C-160-267-22-ND
2223-CFM-4010C-065-251-22-ND
2223-CFM-4010C-150-195-22-ND
2223-CFM-4010C-050-195-22-ND
2223-CFM-4010C-165-251-22-ND
2223-CFM-2507CF-1140-313-22-ND
102-4366-ND
2223-CFM-2006CF-0100-189-20-ND
2223-CFM-8025C-235-364-ND
2223-CFM-8025C-225-290-ND
2223-CFM-9225C-220-269-ND
2223-CFM-9225C-225-317-ND
2223-CFM-8020CF-225-273-ND
2223-CFM-8020CF-235-346-ND
2223-CFM-8020CF-135-346-ND
2223-CFM-7025C-130-332-ND
2223-CFM-7025C-240-394-ND
2223-CFM-7025C-140-394-ND
2223-CFM-7025C-230-332-ND
2223-CBM-5015CF-165-428-ND
2223-CBM-5015CF-175-459-ND
2223-CFM-6025CF-050-351-ND
2223-CFM-7015C-250-406-ND
2223-CFM-9225C-120-269-ND
2223-CFM-3007CF-085-264-ND
2223-CFM-3007CF-0110-320-20-ND
2223-CFM-4010C-050-195-ND
2223-CFM-3510CF-170-222-ND
2223-CBM-5015CF-175-459-22-ND
2223-CFM-2006CF-0100-189-22-ND
2223-CFM-3007CF-085-264-22-ND
2223-CFM-3007CF-060-188-22-ND
2223-CFM-6025CF-135-274-20-ND
2223-CFM-6025CF-250-351-20-ND
2223-CFM-6025CF-035-274-20-ND
2223-CFM-6025CF-235-274-20-ND
2223-CBM-3507CF-145-139-20-ND
2223-CBM-5020C-150-320-20-ND
2223-CFM-7015C-230-295-20-ND
2223-CBM-3507CF-055-183-20-ND
102-4633-ND
2223-CFM-2010CF-060-066-20-ND
2223-CBM-4007C-035-218-ND
102-4361-ND
2223-CFM-5015CF-130-224-ND
2223-CBM-4010C-140-178-22-ND
2223-CFM-4020CF-055-212-22-ND
2223-CFM-4020CF-035-114-22-ND
2223-CFM-4020CF-075-306-22-ND
2223-CBM-3507CF-185-295-ND
2223-CBM-3507CF-065-219-ND
CFM-5015V-247-290-ND
2223-CFM-2507CF-0100-240-22-ND
2223-CFM-2006CF-160-078-ND
2223-CFM-6010C-140-278-ND
2223-CFM-4010C-250-195-ND
2223-CBM-5020C-160-360-20-ND
2223-CFM-8025C-230-330-20-ND
2223-CFM-9225C-230-356-20-ND
2223-CFM-8025C-125-290-20-ND
2223-CFM-8025C-135-364-20-ND
2223-CFM-9225C-130-356-20-ND
2223-CFM-6025CF-050-351-20-ND
2223-CFM-8020CF-125-273-20-ND
2223-CBM-5015CF-165-428-20-ND
2223-CFM-2507CF-050-089-20-ND
2223-CFM-3007CF-060-188-20-ND
2223-CFM-4010C-180-296-22-ND
2223-CFM-4010C-250-195-22-ND
2223-CFM-4010C-080-296-22-ND
2223-CFM-4010C-265-251-22-ND
2223-CBM-4007C-150-238-ND
2223-CBM-4007C-050-238-ND
CFM-4020V-050-165-11-ND
CFM-4020V-060-210-11-ND
CFM-4020V-070-255-11-ND
CFM-4020V-150-165-11-ND
CFM-4020V-160-210-11-ND
CFM-4020V-170-255-11-ND
CFM-4020V-180-275-11-ND
CFM-4020V-170-255-20-ND
2223-CFM-2010CF-1120-217-ND
2223-CFM-2010CF-0120-217-ND
2223-CFM-4010C-165-251-ND
2223-CBM-4007C-065-295-20-ND
2223-CFM-2010CF-1170-292-22-ND
2223-CFM-6025CF-265-408-ND
2223-CFM-6025CF-165-408-ND
2223-CFM-8020CF-245-401-ND
2223-CFM-8020CF-145-401-ND
2223-CBM-4007C-035-218-20-ND
2223-CFM-2507CF-170-163-20-ND
2223-CFM-2507CF-0140-313-22-ND
2223-CFM-7015C-150-406-20-ND
2223-CBM-3507CF-165-219-20-ND
2223-CBM-3507CF-085-295-20-ND
CFM-6015V-239-292-ND
2223-CFM-2006CF-0150-277-22-ND
2223-CFM-2010CF-0170-292-22-ND
CFM-4020V-260-210-ND
CFM-6020V-142-280-ND
2223-CBM-4007C-150-238-20-ND
2223-CBM-4007C-050-238-20-ND
2223-CFM-4020CF-275-306-22-ND
2223-CFM-4020CF-235-114-22-ND
2223-CFM-4020CF-095-342-22-ND
2223-CFM-4020CF-255-212-22-ND
2223-CFM-3510CF-190-277-22-ND
2223-CBM-7530CF-230-404-ND
2223-CFM-4010C-265-251-20-ND
2223-CFM-6025CF-165-408-20-ND
2223-CBM-7530CF-220-282-20-ND
2223-CFM-2507CF-1100-240-22-ND
102-5593-ND
CFM-9225V-117-177-ND
CFM-8025V-120-204-ND
2223-CFM-4010C-280-296-22-ND
2223-CFM-4020CF-295-342-22-ND
2223-CBM-7530CF-240-454-ND
2223-CFM-6010C-140-278-22-ND
2223-CFM-6010C-130-215-22-ND
2223-CFM-2006CF-160-078-22-ND
CFM-5015V-138-201-ND
102-5597-ND
102-4365-ND
CFM-5010V-143-260-ND
CFM-4010V-158-206-ND
2223-CFM-4010C-280-296-20-ND
102-4632-ND
102-5609-ND
2223-CBM-4007C-135-218-ND
102-4362-ND
2223-CFM-4010C-180-296-20-ND
2223-CBM-3507CF-155-183-22-ND
2223-CBM-3507CF-045-139-22-ND
2223-CBM-3507CF-055-183-22-ND
2223-CBM-3507CF-145-139-22-ND
2223-CBM-5015CF-135-293-22-ND
2223-CBM-5015CF-145-348-22-ND
2223-CBM-5015CF-035-293-22-ND
2223-CFM-2006CF-1150-277-22-ND
CFM-4020V-260-210-11-ND
CFM-4020V-270-255-11-ND
CFM-4020V-280-275-11-ND
2223-CFM-3510CF-160-188-20-ND
CFM-5015V-132-154-20-ND
CFM-8025V-129-300-20-ND
2223-CBM-4010C-150-227-22-ND
102-4371-ND
2223-CFM-4010C-150-195-ND
2223-CFM-A225C-115-287-ND
2223-CFM-A225C-015-287-ND
2223-CFM-5015CF-130-224-22-ND
2223-CFM-5015CF-145-312-22-ND
2223-CBM-5015CF-155-391-22-ND
2223-CBM-5015CF-055-391-22-ND
2223-CBM-4007C-135-218-20-ND
2223-CBM-5015CF-135-293-20-ND
2223-CFM-2010CF-1170-292-ND
CFM-6025V-238-220-ND
CFM-6025V-245-270-ND
2223-CFM-4010C-080-296-ND
2223-CFM-5015CF-145-312-ND
2223-CFM-2006CF-1100-189-20-ND
2223-CFM-2006CF-160-078-20-ND
2223-CFM-2006CF-060-078-ND
2223-CFM-2010CF-160-066-20-ND
2223-CFM-5015CF-160-374-20-ND
102-5611-ND
CFM-4020V-145-123-20-ND
2223-CBM-3507CF-165-219-22-ND
2223-CBM-3507CF-065-219-22-ND
2223-CBM-5020C-140-305-22-ND
2223-CBM-3507CF-185-295-22-ND
2223-CBM-5020C-150-320-22-ND
2223-CBM-3507CF-085-295-22-ND
102-4385-ND
102-4386-ND
102-4636-ND
2223-CFM-A225C-120-350-20-ND
CFM-5015V-138-201-20-ND
CFM-5015V-161-330-20-ND
CFM-5015V-172-381-20-ND
CFM-5015V-150-290-20-ND
2223-CFM-2507CF-1100-240-20-ND
CFM-5010V-052-300-20-ND
CFM-4010V-170-273-20-ND
CFM-8025V-132-330-20-ND
CFM-5010V-155-310-20-ND
102-5596-ND
CFM-4010V-070-273-20-ND
CFM-6025V-125-107-20-ND
CFM-4010V-058-206-20-ND
2223-CFM-4010C-065-251-20-ND
CFM-4010V-158-206-20-ND
CFM-8025V-126-280-20-ND
CFM-5010V-043-260-20-ND
2223-CFM-2006CF-0150-277-ND
2223-CFM-3510CF-190-277-20-ND
2223-CFM-A225C-018-327-ND
2223-CFM-6015CF-245-332-22-ND
2223-CFM-6015CF-235-278-22-ND
2223-CFM-6015CF-225-204-22-ND
2223-CBM-5020C-160-360-22-ND
2223-CBM-5015CF-165-428-22-ND
2223-CFM-2006CF-060-078-20-ND
CFM-9225V-127-320-20-ND
2223-CFM-4020CF-235-114-ND
2223-CFM-4020CF-055-212-ND
2223-CBM-4007C-035-218-22-ND
102-4368-ND
2223-CFM-2010CF-0170-292-20-ND
2223-CFM-2507CF-1140-313-ND
2223-CFM-2010CF-0120-217-22-ND
2223-CFM-2006CF-1100-189-ND
2223-CBM-4007C-135-218-22-ND
2223-CBM-4007C-050-238-22-ND
2223-CBM-4007C-065-295-22-ND
2223-CFM-6015CF-235-278-20-ND
2223-CFM-6015CF-225-204-20-ND
2223-CFM-6015CF-255-375-22-ND
2223-CFM-6015CF-245-332-ND
2223-CFM-4020CF-275-306-ND
CFM-9225V-124-280-20-ND
CFM-9225V-130-340-20-ND
2223-CFM-3007CF-060-188-ND
2223-CFM-4020CF-255-212-20-ND
2223-CFM-4020CF-035-114-20-ND
CFM-6010V-135-250-ND
2223-CFM-6010C-130-215-20-ND
2223-CFM-6015CF-255-375-20-ND
2223-CFM-2010CF-1120-217-20-ND
102-5592-ND
102-4635-ND
102-4363-ND
2223-CFM-4020CF-095-342-ND
2223-CBM-4010C-160-267-ND
102-5610-ND
102-5614-ND
CFM-9225V-224-280-ND
2223-CFM-9225C-125-317-20-ND
2223-CFM-2507CF-0140-313-ND
2223-CFM-6015CF-245-332-20-ND
CFM-8025V-226-280-20-ND
2223-CFM-6025CF-135-274-ND
2223-CFM-2507CF-0100-240-20-ND
2223-CFM-7015C-240-357-ND
2223-CFM-3007CF-085-264-20-ND
2223-CFM-2010CF-160-066-22-ND
2223-CFM-2006CF-0100-189-ND
2223-CFM-7015C-240-357-22-ND
2223-CFM-7015C-230-295-22-ND
2223-CFM-8015CF-120-213-20-ND
102-4388-ND
2223-CFM-7015C-130-295-ND
102-4378-ND
2223-CFM-4020CF-075-306-20-ND
2223-CFM-4020CF-295-342-20-ND
2223-CFM-8025C-125-290-ND
2223-CFM-7025C-130-332-20-ND
2223-CFM-2006CF-1150-277-20-ND
2223-CFM-7025C-230-332-20-ND
102-4367-ND
2223-CFM-8015CF-230-301-20-ND
2223-CFM-8015CF-130-301-20-ND
2223-CFM-7015C-040-357-ND
2223-CFM-7015C-140-357-22-ND
2223-CFM-7015C-040-357-22-ND
2223-CFM-6025CF-050-351-22-ND
2223-CFM-6025CF-035-274-22-ND
2223-CFM-6025CF-135-274-22-ND
2223-CFM-6025CF-150-351-22-ND
2223-CFM-7015C-250-406-22-ND
2223-CFM-8015CF-230-301-22-ND
2223-CFM-8015CF-220-213-22-ND
2223-CFM-8015CF-130-301-22-ND
2223-CFM-8015CF-120-213-22-ND
2223-CFM-6025BF-235-274-20-ND
CFM-7015V-128-265-20-ND
2223-CFM-2507CF-050-089-22-ND
CFM-7015V-123-215-20-ND
2223-CFM-8015CF-130-301-ND
2223-CFM-7015C-140-357-20-ND
2223-CFM-8015CF-240-363-20-ND
2223-CFM-7015C-030-295-20-ND
2223-CFM-8015CF-140-363-20-ND
2223-CFM-6025CF-150-351-20-ND
CFM-9225V-227-320-20-ND
CFM-8025V-232-330-20-ND
102-5613-ND
CFM-8025V-229-300-20-ND
2223-CFM-3007CF-0110-320-22-ND
102-4369-ND
102-4374-ND
2223-CFM-6025CF-250-351-ND
2223-CFM-6025CF-235-274-ND
2223-CFM-2507CF-170-163-22-ND
102-4370-ND
102-4364-ND
102-5599-ND
CFM-6015V-122-145-ND
2223-CFM-2006CF-060-078-22-ND
CFM-6015V-130-213-ND
102-4375-ND
2223-CFM-2010CF-060-066-ND
2223-CFM-8015CF-220-213-20-ND
CFM-6010V-140-285-20-ND
102-5594-ND
CFM-6010V-135-250-20-ND
CFM-6010V-130-205-20-ND
CFM-4020V-050-165-ND
2223-CFM-3510CF-160-188-ND
2223-CFM-9225C-225-317-20-ND
2223-CFM-8020CF-235-346-20-ND
2223-CFM-8025C-130-330-20-ND
2223-CFM-9225C-220-269-20-ND
2223-CFM-9225C-120-269-20-ND
2223-CFM-8020CF-225-273-20-ND
2223-CFM-8020CF-135-346-20-ND
2223-CFM-7015C-150-406-22-ND
2223-CFM-8015CF-240-363-22-ND
2223-CFM-6025CF-235-274-22-ND
2223-CFM-6025CF-165-408-22-ND
2223-CFM-8015CF-140-363-22-ND
2223-CFM-6025CF-250-351-22-ND
CFM-4020V-050-165-20-ND
CFM-4020V-070-255-20-ND
102-4380-ND
CFM-8020V-130-350-ND
CFM-8020V-126-300-ND
2223-CFM-7025C-140-394-20-ND
2223-CFM-9225C-130-356-ND
2223-CFM-7025C-240-394-20-ND
2223-CFM-8020CF-125-273-ND
2223-CFM-8025C-230-330-ND
2223-CFM-8025C-135-364-ND
2223-CBM-5020C-160-360-ND
2223-CFM-9225C-230-356-ND
2223-CFM-2006CF-1150-277-ND
2223-CFM-2006CF-1100-189-22-ND
2223-CBM-3507CF-045-139-20-ND
2223-CBM-5020C-140-305-20-ND
2223-CBM-3507CF-155-183-20-ND
CFM-6020V-131-210-ND
102-5601-ND
CFM-6020V-150-335-ND
2223-CFM-4010C-265-251-ND
2223-CFM-7015C-150-406-ND
2223-CBM-3507CF-165-219-ND
2223-CBM-3507CF-085-295-ND
2223-CBM-4007C-165-295-ND
2223-CBM-4007C-065-295-ND
2223-CFM-2010CF-0170-292-ND
2223-CFM-7015C-050-406-ND
2223-CFM-8020CF-135-346-22-ND
2223-CFM-7025C-130-332-22-ND
2223-CFM-6025CF-265-408-22-ND
2223-CFM-7025C-140-394-22-ND
2223-CFM-8020CF-125-273-22-ND
2223-CFM-A225C-020-350-ND
2223-CBM-7530CF-220-282-22-ND
2223-CFM-2010CF-160-066-ND
102-5598-ND
CFM-6015V-130-213-20-ND
CFM-6015V-147-342-20-ND
2223-CFM-2010CF-0120-217-20-ND
CFM-6015V-139-292-20-ND
2223-CFM-8025C-235-364-20-ND
2223-CFM-8025C-225-290-20-ND
2223-CBM-5015CF-175-459-20-ND
2223-CFM-8020CF-245-401-20-ND
CFM-7020V-126-260-20-ND
CFM-7020V-129-300-20-ND
2223-CFM-8020CF-145-401-20-ND
CFM-7020V-132-330-20-ND
102-5605-ND
CFM-4020V-180-275-20-ND
CFM-4020V-150-165-20-ND
CFM-4020V-060-210-20-ND
CFM-4020V-160-210-20-ND
2223-CBM-7530CF-230-404-22-ND
102-5607-ND
CFM-8020V-133-380-20-ND
102-4372-ND
2223-CFM-3510CF-190-277-ND
2223-CFM-4010C-280-296-ND
2223-CBM-7530CF-220-282-ND
2223-CFM-7015C-050-406-20-ND
102-4373-ND
2223-CBM-3507CF-065-219-20-ND
2223-CBM-3507CF-185-295-20-ND
2223-CBM-4007C-165-295-20-ND
2223-CFM-4010C-250-195-20-ND
2223-CFM-8020CF-145-401-22-ND
2223-CFM-8020CF-235-346-22-ND
2223-CFM-8020CF-225-273-22-ND
2223-CBM-7530CF-240-454-22-ND
2223-CFM-8025C-135-364-22-ND
2223-CFM-8025C-130-330-22-ND
2223-CFM-7025C-230-332-22-ND
2223-CFM-8025C-125-290-22-ND
CFM-8025V-132-330
CFM-5015V-132-154
CFM-5015V-161-330
CFM-5010V-043-260
CFM-6025V-125-107
CFM-4010V-058-206
CFM-4010V-170-273
CFM-8025V-126-280
CFM-8025V-129-300
CFM-6010C-130-215
CFM-4010C-065-251
CFM-6010C-150-326
CFM-7015C-230-295
CBM-5020C-150-320
CFM-9225V-124-280
CFM-4010C-180-296
CFM-2507CF-0100-240
CFM-2507CF-050-089
CFM-8025C-130-330
CFM-4020CF-035-114
CFM-4020CF-255-212
CFM-8015CF-230-301
CFM-6015CF-235-278
CFM-6015CF-225-204
CFM-7015V-128-265
CFM-2507CF-1100-240
CFM-2507CF-170-163
CFM-6015CF-255-375
CFM-8025V-226-280
CBM-4010C-140-178
CFM-5015CF-160-374
CFM-4020CF-075-306
CFM-4020CF-295-342
CBM-5015CF-035-293
CBM-5015CF-045-348
CBM-5015CF-135-293
CBM-5015CF-145-348
CFM-6010V-130-205
CFM-8015CF-220-213
CFM-8015CF-120-213
CBM-5015CF-155-391
CBM-5015CF-055-391
CBM-4010C-150-227
CFM-9225C-125-317
CFM-8015CF-240-363
CFM-6025CF-035-274
CFM-8015CF-140-363
CFM-6025CF-150-351
CFM-7015C-030-295
CFM-7015C-140-357
CBM-3507CF-145-139
CBM-5020C-140-305
CBM-3507CF-045-139
CBM-3507CF-155-183
CBM-3507CF-055-183
CFM-6015V-139-292
CFM-3007CF-0110-320
CFM-4020V-060-210
CFM-4020V-070-255
CFM-4020V-150-165
CFM-4020V-160-210
CFM-8020V-146-480
CFM-5010V-155-310
CFM-8025C-235-364
CFM-8025C-225-290
CFM-9225C-220-269
CFM-9225C-225-317
CFM-8020CF-225-273
CFM-8020CF-235-346
CFM-8020CF-135-346
CFM-7025C-130-332
CFM-7025C-240-394
CFM-7025C-140-394
CFM-7025C-230-332
CBM-5015CF-165-428
CBM-5015CF-175-459
CFM-6025CF-050-351
CFM-7015C-250-406
CFM-9225C-120-269
CFM-3007CF-085-264
CFM-4010C-050-195
CFM-3510CF-170-222
CFM-5015V-172-381
CBM-4007C-035-218
CFM-4010V-070-273
CFM-5015CF-130-224
CBM-3507CF-185-295
CBM-3507CF-065-219
CFM-5015V-247-290
CFM-2006CF-160-078
CFM-6010C-140-278
CFM-4010C-250-195
CBM-4007C-150-238
CBM-4007C-050-238
CFM-2010CF-1120-217
CFM-2010CF-0120-217
CFM-4010C-165-251
CFM-6025CF-265-408
CFM-6025CF-165-408
CFM-8020CF-245-401
CFM-8020CF-145-401
CFM-6015V-239-292
CFM-4020V-260-210
CFM-6020V-142-280
CBM-7530CF-230-404
CFM-4020V-145-123
CFM-9225V-117-177
CFM-8025V-120-204
CBM-7530CF-240-454
CFM-5015V-138-201
CFM-5015V-150-290
CFM-5010V-052-300
CFM-5010V-143-260
CFM-4010V-158-206
CFM-4010V-150-157
CFM-8025V-120-204-20
CBM-4007C-135-218
CFM-4010V-185-314
CFM-6020V-245-335
CFM-4010C-150-195
CFM-A225C-115-287
CFM-A225C-015-287
CFM-2010CF-1170-292
CFM-6025V-238-220
CFM-6025V-245-270
CFM-4010C-080-296
CFM-5015CF-145-312
CFM-2006CF-060-078
CFM-9225V-117-177-20
CFM-8025V-232-330
CFM-9225V-130-340
CFM-9225V-127-320
CFM-5010V-143-260-20
CFM-2006CF-0150-277
CFM-A225C-018-327
CFM-4020CF-235-114
CFM-4020CF-055-212
CFM-6010V-140-285
CFM-2507CF-1140-313
CFM-2006CF-1100-189
CFM-6015CF-245-332
CFM-4020CF-275-306
CFM-3007CF-060-188
CFM-6010V-135-250
CFM-4010V-150-157-20
CFM-7015V-123-215
CFM-4020V-180-275
CFM-4020CF-095-342
CBM-4010C-160-267
CFM-8025V-229-300
CFM-9225V-227-320
CFM-9225V-224-280
CFM-2507CF-0140-313
CFM-6025CF-135-274
CFM-7015C-240-357
CFM-2006CF-0100-189
CFM-9225V-230-340
CFM-7015C-130-295
CFM-8015V-130-347
CFM-8025C-125-290
CFM-5015V-258-330
CFM-7015C-040-357
CFM-8015CF-130-301
CFM-9225V-224-280-20
CFM-6015V-154-362
CFM-7015V-133-315
CFM-6025CF-250-351
CFM-6025CF-235-274
CFM-6015V-254-362
CFM-4020V-280-275
CFM-6015V-147-342
CFM-6015V-122-145
CFM-6015V-130-213
CFM-7020V-132-330
CFM-2010CF-060-066
CFM-4020V-170-255
CFM-4020V-050-165
CFM-3510CF-160-188
CFM-8020V-133-380
CFM-8020V-130-350
CFM-8020V-126-300
CFM-9225C-130-356
CFM-8020CF-125-273
CFM-8025C-230-330
CFM-8025C-135-364
CBM-5020C-160-360
CFM-9225C-230-356
CFM-2006CF-1150-277
CFM-6020V-131-210
CFM-6020V-157-390
CFM-6020V-150-335
CFM-4010C-265-251
CFM-7015C-150-406
CBM-3507CF-165-219
CBM-3507CF-085-295
CBM-4007C-165-295
CBM-4007C-065-295
CFM-2010CF-0170-292
CFM-7015C-050-406
CFM-A225C-020-350
CFM-2010CF-160-066
CFM-6015V-122-145-20
CFM-8015V-127-320
CFM-8020V-126-300-20
CFM-6025V-152-312
CFM-3510CF-190-277
CFM-4010C-280-296
CBM-7530CF-220-282
CFM-6025V-252-312
CFM-A238V-231-480-20-ND
CFM-A238V-221-370-20-ND
CFM-A238V-226-440-ND
CFM-A238V-226-440-20-ND
CFM-A225V-131-445-20-ND
CFM-A225V-122-340-20-ND
CFM-A225V-127-405-20-ND
CFM-A238V-131-480-20-ND
CFM-A238V-121-370-20-ND
102-4357-ND
2223-CFM-A238B-132-480-ND
CFM-A225V-231-445-20-ND
CFM-A225V-222-340-20-ND
102-4360-ND
CFM-A238V-126-440-20-ND
CFM-A238V-126-440-ND
CFM-8025V-148-447-20-ND
CFM-A225V-227-405-20-ND
102-5615-ND
102-4359-ND
2266-CFM-9225V-245-460-ND,102-4389-ND
CFM-9225V-145-455-20-ND
CFM-8025V-145-431-20-ND
CFM-8025V-142-415-20-ND
CFM-7020V-140-375-20-ND
102-4358-ND
2223-CBM-7530CF-260-540-22-ND
102-4376-ND
CFM-9225V-139-416-ND
CFM-8025V-145-431-ND
CFM-9225V-139-416-20-ND
CFM-9225V-142-437-20-ND
2266-CFM-A238V-121-370-11-ND,CFM-A238V-121-370-11-ND
2223-CBM-7530CF-260-540-20-ND
102-4384-ND
2223-CBM-7530CF-260-540-ND
102-4392-ND
102-5612-ND
2223-CFM-9225C-130-356-22-ND
2223-CBM-7530CF-250-493-22-ND
CFM-A238V-221-370-ND
2223-CBM-7530CF-250-493-20-ND
2266-CFM-9225V-145-455-ND,102-4387-ND
2223-CBM-7530CF-250-493-ND
2223-CFM-A225C-020-350-20-ND
CFM-A225V-122-340-ND
CFM-A225V-127-405-ND
CFM-A238V-121-370-ND
2266-CBM-5020V-148-ND,102-5585-ND
2223-CFM-7015C-040-357-20-ND
CFM-A225V-222-340-ND
2223-CFM-9225C-125-317-22-ND
102-5586-ND
2223-CFM-2010CF-1120-217-22-ND
2223-CFM-2010CF-1170-292-20-ND
2223-CBM-4007C-165-295-22-ND
2223-CBM-4007C-150-238-22-ND
102-5603-ND
CFM-6025V-252-312-20-ND
CFM-6025V-245-270-20-ND
CFM-6025V-238-220-20-ND
CFM-6025V-152-312-20-ND
CFM-8015V-230-347-20-ND
102-5606-ND
102-5602-ND
CFM-6020V-237-280-20-ND
2223-CFM-A225C-220-350-20-ND
2223-CFM-A225C-115-287-20-ND
CFM-8025V-142-415-ND
2223-CFM-A225C-018-327-20-ND
2223-CFM-5015CF-160-374-22-ND
2223-CFM-2010CF-060-066-22-ND
CFM-6025V-231-167-ND
CFM-8015V-227-320-20-ND
2223-CFM-2006CF-0150-277-20-ND
CFM-6020V-245-335-20-ND
CFM-6020V-230-230-ND
2223-CFM-A225C-220-350-ND
2223-CFM-A225C-120-350-ND
CFM-6020V-237-280-ND
CFM-8020V-230-350-20-ND
CFM-8020V-233-380-20-ND
CFM-8020V-226-300-20-ND
2223-CFM-9225C-220-269-22-ND
2223-CFM-9225C-230-356-22-ND
2223-CFM-9225C-225-317-22-ND
2223-CFM-A225C-020-350-22-ND
2223-CFM-A225C-220-350-22-ND
2223-CFM-A225C-015-287-20-ND
CFM-6025V-131-167-20-ND
CFM-4020V-260-210-20-ND
CFM-6020V-150-335-20-ND
CFM-4020V-280-275-20-ND
CFM-6015V-239-292-20-ND
CFM-6025V-138-220-20-ND
CFM-6020V-142-280-20-ND
CFM-6025V-145-270-20-ND
CFM-6015V-154-362-20-ND
CFM-7020V-232-330-20-ND
2223-CBM-7530CF-230-404-20-ND
2223-CFM-9225C-120-269-22-ND
2223-CFM-8020CF-245-401-22-ND
2223-CFM-8025C-225-290-22-ND
2223-CFM-8025C-230-330-22-ND
2223-CFM-8025C-235-364-22-ND
2223-CFM-A225C-015-287-22-ND
2223-CFM-A225C-120-350-22-ND
2223-CFM-A225C-018-327-22-ND
2223-CFM-A225C-115-287-22-ND
CFM-8015V-130-347-20-ND
CFM-8015V-127-320-20-ND
CFM-8020V-226-300-ND
CFM-7020V-229-300-20-ND
CFM-5015V-258-330-20-ND
CFM-5015V-247-290-20-ND
2223-CFM-6025CF-265-408-20-ND
CFM-9225V-230-340-20-ND
CFM-6015V-254-362-20-ND
CFM-4020V-270-255-20-ND
CFM-6020V-157-390-20-ND
CFM-6020V-131-210-20-ND
CFM-6015V-247-342-20-ND
CFM-7015V-133-315-20-ND
2223-CFM-6010C-150-326-22-ND
102-5600-ND
102-4634-ND
CFM-6025V-131-167-ND
102-5595-ND
CFM-6025V-138-220-ND
2223-CFM-3510CF-170-222-20-ND
2223-CFM-7025C-240-394-22-ND
102-4373-ND
102-4372-ND
102-5607-ND
102-5605-ND
102-5598-ND
102-5601-ND
102-4380-ND
102-5594-ND
102-4375-ND
102-4370-ND
102-4364-ND
102-5599-ND
102-4369-ND
102-4374-ND
102-5613-ND
102-4367-ND
102-4378-ND
102-4388-ND
102-4363-ND
102-5610-ND
102-5614-ND
102-5592-ND
102-4635-ND
102-4368-ND
102-5596-ND
102-4386-ND
102-4636-ND
102-4385-ND
102-5611-ND
102-4371-ND
102-4362-ND
102-4632-ND
102-5609-ND
102-4365-ND
102-5597-ND
102-5593-ND
102-4361-ND
102-4633-ND
CFM-A238V-226-440
CFM-A225V-131-445
CFM-A238B-132-480
CFM-A238V-231-480
CFM-A238V-126-440
CFM-A225V-227-405
CFM-A238V-131-480
CFM-9225V-245-460
CFM-A225V-231-445
CFM-7020V-146-415
CFM-9225V-139-416
CFM-8025V-145-431
CFM-8025V-148-447
CBM-7530CF-260-540
CBM-5020V-152
CFM-9225V-142-437
CFM-A238V-221-370
CFM-9225V-145-455
CBM-7530CF-250-493
CFM-A225V-122-340
CFM-A225V-127-405
CFM-A238V-121-370
CBM-5020V-148
CFM-A225V-222-340
CBM-6015V-144
CFM-6025V-231-167-20
CFM-8015V-224-308-20
CFM-6020V-230-230-20
CFM-8025V-142-415
CFM-6025V-231-167
CFM-6020V-230-230
CFM-A225C-220-350
CFM-A225C-120-350
CFM-6020V-237-280
CFM-8020V-226-300
CFM-6015V-247-342
CFM-6025V-145-270
CFM-6025V-131-167
CFM-4020V-270-255
CFM-6025V-138-220
CFM-6025V-252-312
CFM-6025V-152-312
CFM-3510CF-190-277
CFM-4010C-280-296
CBM-7530CF-220-282
CFM-8015V-127-320
CFM-2010CF-160-066
CFM-A225C-020-350
CFM-7015C-050-406
CFM-2010CF-0170-292
CFM-7015C-150-406
CBM-3507CF-165-219
CBM-3507CF-085-295
CBM-4007C-165-295
CBM-4007C-065-295
CFM-6020V-131-210
CFM-6020V-157-390
CFM-6020V-150-335
CFM-4010C-265-251
CFM-2006CF-1150-277
CFM-9225C-130-356
CFM-8020CF-125-273
CFM-8025C-230-330
CFM-8025C-135-364
CBM-5020C-160-360
CFM-9225C-230-356
CFM-8020V-133-380
CFM-8020V-130-350
CFM-8020V-126-300
CFM-3510CF-160-188
CFM-4020V-170-255
CFM-4020V-050-165
CFM-2010CF-060-066
CFM-7020V-132-330
CFM-6015V-254-362
CFM-4020V-280-275
CFM-6015V-147-342
CFM-6015V-122-145
CFM-6015V-130-213
CFM-6015V-154-362
CFM-7015V-133-315
CFM-6025CF-250-351
CFM-6025CF-235-274
CFM-8015CF-130-301
CFM-7015C-040-357
CFM-5015V-258-330
CFM-8025C-125-290
CFM-7015C-130-295
CFM-8015V-130-347
CFM-9225V-230-340
CFM-2006CF-0100-189
CFM-6025CF-135-274
CFM-7015C-240-357
CFM-2507CF-0140-313
CFM-4020V-180-275
CFM-4020CF-095-342
CBM-4010C-160-267
CFM-8025V-229-300
CFM-9225V-227-320
CFM-9225V-224-280
CFM-7015V-123-215
CFM-6010V-135-250
CFM-3007CF-060-188
CFM-6015CF-245-332
CFM-4020CF-275-306
CFM-2006CF-1100-189
CFM-2507CF-1140-313
CFM-6010V-140-285
CFM-4020CF-235-114
CFM-4020CF-055-212
CFM-A225C-018-327
CFM-2006CF-0150-277
CFM-9225V-130-340
CFM-9225V-127-320
CFM-8025V-232-330
CFM-2006CF-060-078
CFM-4010C-080-296
CFM-5015CF-145-312
CFM-6025V-238-220
CFM-6025V-245-270
CFM-2010CF-1170-292
CFM-A225C-115-287
CFM-A225C-015-287
CFM-4010C-150-195
CFM-6020V-245-335
CFM-4010V-185-314
CBM-4007C-135-218
CFM-4010V-150-157
CFM-5010V-052-300
CFM-5010V-143-260
CFM-4010V-158-206
CFM-5015V-138-201
CFM-5015V-150-290
CBM-7530CF-240-454
CFM-4020V-145-123
CFM-9225V-117-177
CFM-8025V-120-204
CBM-7530CF-230-404
CFM-4020V-260-210
CFM-6020V-142-280
CFM-6015V-239-292
CFM-8020CF-245-401
CFM-8020CF-145-401
CFM-6025CF-265-408
CFM-6025CF-165-408
CFM-4010C-165-251
CFM-2010CF-0120-217
CFM-2010CF-1120-217
CBM-4007C-150-238
CBM-4007C-050-238
CFM-4010C-250-195
CFM-6010C-140-278
CFM-2006CF-160-078
CFM-5015V-247-290
CBM-3507CF-185-295
CBM-3507CF-065-219
CFM-5015CF-130-224
CFM-4010V-070-273
CBM-4007C-035-218
CFM-5015V-172-381