The Siemens S7-1200 G2 PLC has two 100BASE-T PROFINET ports. Each link uses four conductors: one pair for receive and one pair for transmit.
This engineering brief explores the subtle physical and application differences between a 2-pair PROFINET (100BASE-T) and a 4-pair Ethernet (1000BASE-T) as used in industrial automation. The Siemens S7-1212FC G2 PLC along with the featured LAPP PROFINET cable is shown in Figure 1.
This article is part of a larger cluster.
-
Essential Shop Practices
-
Logistics for LAPP Cable and Connectors
You are encouraged to review the documentation provided by PI North America. There you will find clear documents describing PROFINET technology as well as training.
Key Takeaways
- PROFINET cable is Ethernet cable.
- As a rule, 100BASE-T required 2-pair while 1000BASE-T required 4-pair.
- The new Siemens S7-1212FC G2 PLC supports 2-pair 100BASE-T for PROFINET and PROFIsafe. The 2-pair LAPP PROFINET cable is a good match.
- PROFINET requires system-level thinking including both cable, connectors, and associated components such as the PLC.
- Stop thinking about PROFINET cable in terms of future speed upgrades. Instead think about suitability for a given industrial application.
This article is part of the DigiKey Field Guide for Industrial Automation
Location: Teach It → Shop Practices
Difficulty:
Student — difficulty levels explained
Author: Aaron Dahlen | MSEE | Senior Applications Engineer, DigiKey
Last update: 09 Nov 2026
Figure 1: Image of a Siemens S7-1212FC G2 safety PLC and a LAPP RJ45 PROFINET connector.
Start at the PLC
The Siemens S7-1200 G2 is a representative PROFINET-enabled PLC. The pinout for the PLC’s RJ45 ports as described in the System Manual is included as Figure 2.
Observe:
- Ethernet (RJ45 connector) are used.
- Only two data pair are used including 1 & 2 as well as 3 & 6.
- All other pins are grounded.
- A suitable 4-pair cable may be used but it will not provide a speed increase beyond 100BASE-T.
- Supports full-duplex operation at 100 Mbps.
- The Siemens system manual specifies CAT 5e shielded.
Figure 2: Physical port mapping for the Siemens S7-1200 G2 PLC.
Tech Tip: Verify the PLC’s port capability before purchasing cable as not all PLC ports have the same capability.
An example is the Schneider TM262L20MESE8T shown in Figure 3. Technically, the Schneider speaks EtherNet/IP and Modbus TCP (not PROFINET). However, the concepts are the same. It uses a 100BASE-T for Ethernet 1 and includes two 1000BASE-T ports for Ethernet 2. As another example, consider the new to DigiKey Siemens S7-1500 compact CPU type 6ES75111CK010AB0. Like the S7-1200 G2 from Figure 1, it has two built-in 100BASE-T PROFINET ports. Its capabilities may be expanded by adding a 6GK7545-1GX10-0XE0 communications processor featuring a 1000BASE-T port.
These three port PLCs are at the intersection of IT and OT.
Figure 3: Image of a Schneider PLC featuring three Ethernet ports including a single 100BASE-T and a pair of 1000BASE-T ports.
What is CAT 5e industrial cable?
The terms CAT 5 is incomplete and can lead to incorrect assumptions. For example in the IT world, there is an instinct to view CAT 5e cable as somewhat dated. Yet, it is still recognizable as a 4-pair (8 wire) cable designed for 1000BASE-T systems. While this is true, we need to go back several decades to understand CAT 5 (not CAT 5 enhanced) as it was originally implemented.
In the 1990s CAT 5 cable was commonly used for 100BASE-T. While most cables included 4-pair, only two were actively used: one for transmit and one for receive. This is exactly what we see in the in the Siemens PLC (Figure 2) and the physical cable as shown in Figure 4. I assure you, the lower cable in Figure 4 is PROFINET, specifically LAPP type 2170891.
Figure 4: Comparison of 4-pair LAPP CAT 6A (top) Ethernet and the 2-pair CAT 5e (Bottom) PROFINET cables.
Tech Tip: The featured PROFINET cable will fail when tested using a conventional 4-pair Ethernet cable tester. Instead, the tester should shod continuity for the shield and pins 1, 2, 3 and 6. All other wires will test as opens.
Figure 5: Top of datasheet for the LAPP type 2170891 PROFINET cable showing the star quad wire configuration.
Tech Tip: As a general rule, the 4-pair Ethernet cable is electrically compatible with PROFINET. However, the reverse is not always true as the fast 1000BASE-T requires all four pair.
Physical suitability is an entirely different question. Here, cables are rated by jacket type (PVC vs PUR) for environmental durability. They are also rated to handle bending and torsion forces.
IMO, the electrical characteristics are the least interesting part of the cable selection process. This is especially true when we consider the application specific requirements for cable and even connector type. Refer to this article for additional guidance.
If Both 4-pair and 2-pair are available why does 2-pair PROFINET exist?
In the IT world, we generally select cables with an eye toward future capability. CAT 6A or even CAT 7 are strong contenders. We may not need the speed capability today, yet the cost may be justified.
STOP!
OT is not IT.
As a data point, consider this document from PI that shows the certification for the Siemens S7-1200 G2.
S7_1200_PROFINET_Certification.pdf (182.8 KB)
While network speed is important, industrial networks that use the S7-1200 G2 need to focus on other system attributes.
- Electrical interference: Industrial machinery generates considerable noise that can impact PROFINET communications. For example even a shielded copper cable can pick up interference from high power feeder conductors, VFD to motor feed cables, contactors, and motors. This requires us to think in system terms to consider both the cable and the nodes such as the PLC.
- Durability: The “star quad” shown in Figure 5 is a relatively simple construction when compared to a 4-pair cable. All things being equal, the simple star-quad cable should be more reliable. It has half the wires, half the number of terminations, and the conductors have a larger diameter. However things are not equal, and that is the beauty of industrial PROFINET. The featured LAPP 2170891 PROFINET cable is designed for fixed installations. Cables such as LAPP’s 2170894 are designed for “continuously flexing use in moving machine part…”
- Cable installation: This is where things get really interesting. Figure 1 shows a LAPP type 21700651 connector. This is one of many LAPP RJ45 connectors as outlined in this article. In this case, both the cable and the associated RJ45 connector become significant system components when we consider the angle of the cable as it connects to equipment such as the PLC.
For additional information about LAPP cables please see Video 1.
Video 1: Introduction to PROFINET cables.