Building a State Machine in Siemens TIA Portal
This engineering brief presents a Siemens TIA Portal UDFB designed to control and monitor a motor starter. We will also highlight some of the TIA Portal functionality that makes the numeric state machine easier to develop and troubleshoot.
The reader is assumed to have a basic knowledge of the Siemens PLC with a good understanding of ladder logic up to and including operation of the move function block.
Also, note that the code was developed and tested on a Siemens S7-1200 CPU 1215 FC.
Difficulty: :gear: Engineer — difficulty levels explained
Last update: 06 Mar 2026
Control of the Motor Starter
There are many ways to control a large industrial motor starter from the PLC’s perspective. They range from simple open loop control via an output pin all the way to network-based solutions that control and then monitor individual phase currents.
In this note, we will close the loop to verify that the motor starter has activated. This is done using the UDFB as seen in Figure 1. Specifically, upon receipt of the xEnable signal, the UDFB’s xCoilDrive output line is activated. An auxiliary contact from the motor starter is then fed back to the UDFB’s xSensor input.
Figure 1: The motor starter is instantiated with time-based test values set for human interaction.
Tech Tip: The UDFB may be classified as either edge-sensitive or level-sensitive. An edge sensitive UDFB will be triggered (start) on a rising or falling edge while a level-sensitive block will be active while the input is active. Identification of the UDFB type is essential to understand and to then troubleshoot the block:
  • Edge triggered: Activates on a pulse (rising or falling edge depending on the design) and runs to completion or until aborted.
  • Level-sensitive: Actives only when the enable signal is present.
The UDFB featured in this article is level-sensitive. The motor starter’s xCoilDrive signal will be active when the xEnable signal is present.
Motor Starter States
There are five states incorporated into the UDFB. The rudimentary failure associated with each state may be detected by monitoring the feedback from the motor starter’s auxiliary contacts.
  1. Open: The motor starter is in an inactive state with no power applied to the contactor’s coil. The UDFB will enter a fault state if the motor starter unexpectedly closes for longer than timGlitch. This could occur when a technician uses an insulated screwdriver to force the motor starter’s armature.
  2. Closing: The motor starter’s contactor is transitioning from an open to a physically closed state. The UDFB will enter a fault state if the contacts fail to close within timClose. Figure 1 shows the UDFB that has faulted from this state.
  3. Closed: The motor starter on the associated motor is running. The UDFB will enter a fault state if the sensor signal is momentarily lost for a period longer than timGlitch. This fault could be caused by a loose drive wire leading to the motor starter or the feedback line. It could also be caused by an overload event which would trip the motor starter via the thermal overload block.
  4. Opening: The motor starter’s contactor is transition from a closed to an open state. A fault is triggered if the contacts do not open within timClose as this implies that the primary or interposing relay contacts have been welded together.
  5. Fault: The motor starter is in a fault condition. It will be released when the enable signal is disabled and the reset button is pressed.
Ladder Logic State Encoding
There are several different ways of encoding states in ladder logic ranging from latches, set reset coils, all the way to numeric representation of the state. Our 5-state example could be constructed using any of the three methods. However, in my opinion the numeric method as shown in Figures 2 and 3 is the easiest to understand. I’ll admit that this could reflect my background in embedded programming where I prefer to encode states in a tree structure using the C programming’s switch-case statement.
Enumerated Data Types in Ladder Logic
It is easy to lose track of numeric states if we rely entirely on numbers. For example, referring to the closing state as the decimal number 1 has no intrinsic meaning. However, if we add abstraction, we can substitute a meaningful keyword for the number.
The Siemens TIA Portal provides a convenient enumeration method using constants as highlighted in Figure 2. Here we see that each state has a meaningful name. An example is the mapping of uiStClosing to the value of 1. In this example we are using Hungarian notation with prefix unsigned integer (ui) and state (st).
Figure 2: State encoding used for the UDFB states.
The power of these enumerated states is shown in Figure 3 which shows the ladder logic network for the closing state. The network begins with a comparison operator to determine if uiState variable is equal to the uiStClosing constant—are we in state 1? Assuming we are in the closing state, there are three ways to exist including a jump to:
  • state closed: This is the natural progression as the motor starter transition from open to closed.
  • state fault: This occurs when the motor starter feedback is not asserted before timClose.
  • state opening: This transition occurs when the operator quickly changes their mind and attempts to open the contactor before it has fully entered the closed state.
Note that the logic includes a string move function (S_MOVE) that will copy “failed to close” to the strFaultCondition character array. This provides the technician a clear explanation for condition leading to the UDFB’s fault condition. This information may also be used for a larger HMI alarm system if additional code is used to consolidate the fault strings.
Figure 3: Network for the UDFB’s closing state with state next logic on the first three branches and the output logic on the last branch.
Tech Tip: Figure 3 includes several series connected set and reset coils. This provides a convenient and compact way to incorporate the output logic into each network. Please refer to this TechForum post for additional considerations for series connected coils and placement of set/reset coils. As described in the article, many people have strong feelings against the series-connected coils and the set/reset coils.
State Machine Symmetry and Design Overview
The numeric-based state machine is surprisingly compact and symmetrical with each state being closely related to other states. Each state closely follows Figure 3 (the closing state) with clear conditional jumps to other states with emphasis on clarity through enumeration.
If you can follow Figure 3, I am confident that the other states will be easy to follow. Further exploration of the remaining states is left as a homework assignment. Also, you are encouraged to download this PDF copy of the motor controller.
UDFB.pdf (88.1 KB)
Fault State Logic
Before departing, we will briefly examine the fault state as shown in Figure 4. As before, we begin with a test for equality—are we in the fault state. This is followed by two branches:
  • If the motor starter is turned off (not enabled) and the reset button is pressed, we jump to the open (idle) state.
  • The last branch updates the UDFB’s blocks using series-connected set and reset coils.
Note that the motor starter must be turned off before the system can be reset. This prevents unexpected motor starts as the operator or technician must deliberately turn the system off.
Figure 4: Logic for the fault state.
Parting Thoughts
A state machine may be constructed using a numeric state variable. This yields compact code perfect for UDFB encapsulation. In the featured example, each network encapsulates the state next transition as well as the output logic for each state.
While the featured code is still relatively simple, the method scales well when compared to alternatives such as latches and the set/reset coils. For example, a reversing motor starter would double in size. Yet, it is easy to follow the logic for each state network.
We would love to hear from you. Do you have a preferred programming method? Please leave your thoughts in the comments section. Also, give a like if you learned something from this post.
Best wishes,
:books: Continue Exploring Industrial Control Systems
:world_map: DigiKey Navigation
:japanese_symbol_for_beginner: Related Foundational Articles
About This Author
Learning Companion for a Ladder Logic Based User-Defined Function Block
SiemensのTIAポータルを使用したユーザー定義ファンクションブロック(UDFB)の構築
Programming Siemens GRAPH: Moore Machine Pattern
LD UDFB Guided Learning Q01: – What Is a State Machine?
什麼是 Siemens ET 200SP 電位組?
PLC Languages in the Classroom and AI-Assisted Program Design
What is a Siemens ET 200SP Potential Group?
Building a State Machine in Structured Text using Siemens TIA Portal
Building a State Machine in Function Block Diagram using Siemens TIA Portal
LD UDFB Guided Learning Q09: – Identify the implicit one shot in a state machine
What is a motor starter’s solid-state overload relay?
How to Configure the FirstScan Bit in Siemens TIA Portal
Make Your PLC Play a Song: Mastering Siemens PLC Memory Arrays
Integrating the Banner WLF12 Flexible LED Light Strip with a PLC
LD UDFB Guided Learning Q13: Modify the featured UDFB so that a single timer resource is used
LD UDFB Guided Learning Q12: Should we use unsigned int or double as the state variable?
Using UDTs to Enforce Structure in PLC Programs
Field Guide to Industrial Automation and Control
Siemens PLC and Automation Technical Briefs
PLC Response Time Explained: Hardware Interrupts vs the Scan Cycle
Module 5 Pathway: Engineer: PLC Architecture and Program Structure
什麼是馬達起動器的固態過載繼電器?
Understanding the Siemens Data Block (DB) File Format in TIA Portal
What is the best PLC language for data processing?
LD UDFB Guided Learning Q02: – Advantages of a Latch, Set Reset Coils, and Numeric Methods
LD UDFB Guided Learning Q03: – Describe UDFB mapping and memory
LD UDFB Guided Learning Q04: – Define Enumeration as Related to a PLC-based State Machine
LD UDFB Guided Learning Q05: – Difference Between Edge-Triggered and Level-Sensitive UDFB
LD UDFB Guided Learning Q06: – How is PLC-based numeric state machine similar a C case-switch?
LD UDFB Guided Learning Q07: – Construct bubbles and arrows representation of the state machine
LD UDFB Guided Learning Q08: – What would happen if the NOT xEnable condition were removed
LD UDFB Guided Learning Q10: Select appropriate values for timGlitch and timMove in a motor starter?
LD UDFB Guided Learning Q11: – What is state fall through for a state machine?
LD UDFB Guided Learning Q14: – How to account for a motor overload
LD UDFB Guided Learning Q16: – How can a UDFB's fault status string be used with an HMI?
LD UDFB Guided Learning Q15: – Modify the state machine to drive a dual-coil DCVA